Hi,
** First of all let me state that a professional will be doing the work I just want a sanity check on what I think I need... **
So, we're getting an EV and need to install a 7.5KW charger.
We currently have a 60A main fuse going into a CU with 100A RCD. We know we need to get the main fuse upgraded, as well as the tails from the main fuse to the CU. Ok with this, unless anyone thinks I'm wrong?
In the CU I have a 32A MCB then running in an underground duct to the garage where there a smaller CU with a current 16A (I think) MCB and a free MCB. However the cable is only 6mm2. The EV chargepoint is wanted in or near the garage, so it seems logical to add the capability to the garage for the EV chargpoint in addition to what I already have in the garage (16A MCB I think).
So what I'm proposing is:
- Upgrade tails and main fuse for 100A
- Break out the feed before the current CU and add a 60A(?) switched main, which then feeds the submain in the garage
- Upgrade underground cable to 16mm2 (total length <20m)
- Update the CU in the garage with an additional 32A MCG for the EV point, plus I think a single 16A MCB I already have feeding the garage.
Have I missed anything? As stated at the top of the page I just want to sanity check what I think I need, a pro will be doing the work.
** First of all let me state that a professional will be doing the work I just want a sanity check on what I think I need... **
So, we're getting an EV and need to install a 7.5KW charger.
We currently have a 60A main fuse going into a CU with 100A RCD. We know we need to get the main fuse upgraded, as well as the tails from the main fuse to the CU. Ok with this, unless anyone thinks I'm wrong?
In the CU I have a 32A MCB then running in an underground duct to the garage where there a smaller CU with a current 16A (I think) MCB and a free MCB. However the cable is only 6mm2. The EV chargepoint is wanted in or near the garage, so it seems logical to add the capability to the garage for the EV chargpoint in addition to what I already have in the garage (16A MCB I think).
So what I'm proposing is:
- Upgrade tails and main fuse for 100A
- Break out the feed before the current CU and add a 60A(?) switched main, which then feeds the submain in the garage
- Upgrade underground cable to 16mm2 (total length <20m)
- Update the CU in the garage with an additional 32A MCG for the EV point, plus I think a single 16A MCB I already have feeding the garage.
Have I missed anything? As stated at the top of the page I just want to sanity check what I think I need, a pro will be doing the work.